Question : Modbus address range
Hi, i am required to communicate with some modbus devices via tcp, i understand that i need to assign modbus addresses to these devices so i can get my data correctly. I read that the address range is from 400001 to 49999. i am just doing read only communications (i.e getting data from the devices) both analog and digital.
This is what i am doing now.
Generator running status - 400101
Engine speed - 400102
Common Fault - 400103
thanks
Answer : Modbus address range
> no ans to my question
Well, you didn't really ask a question.
You indicated you wanted to assign modbus addresses to some discrete devices, but that's not necessary.
Their inputs were already appearing in those 3 registers. They were technically assigned addresses as soon as they were wired to the programmable controller's input cards, and to access their data all you needed were those register addresses.